Water damage in my garage near the water heater

Closed Thread
Thread Tools
  #16  
Old 02-01-2022, 07:49 AM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 16,780
Thanks: 2,914
Thanked 16,013 Times in 6,275 Posts
Default

Quote:
Originally Posted by mamamia54 View Post
Our water heater does not have an expansion tank. What does an expansion do and are they really necessary?
Yes, the expansion tank is necessary. It is required by the building code, but some older houses do not have them because the code was not in effect at that time. And, some plumbers will replace an old water heater and neglect to add the expansion tank. The expansion tank provides an air cushion in your water system to maintain a safe water pressure. When the tank heats up, the water expands a little and, without an expansion tank, the pressure can get too high, especially if all of your plumbing fixtures are turned off. The expansion tank should contain half water and half air, so the water can expand into the expansion tank and the pressure does not increase. The pressure in the expansion tank is normally set at about 60 psi. The expansion tank protects both the water heater and all of the plumbing fixtures in your house from damage due to excessive water pressure. When replacing your water heater, it is a good idea to require the plumber to include an expansion tank in their price quote.
  #17  
Old 02-01-2022, 07:53 AM
Randyj66 Randyj66 is offline
Member
Join Date: May 2018
Posts: 39
Thanks: 0
Thanked 45 Times in 20 Posts
Default

If you have public water and not a well, a expansion tank is necessary and code required because essentially you have a closed system because of back flow check valves in the water supply.The tank is designed to absorb the excess pressure of the hot water because of thermal expansion. If not installed it stresses the system with too much pressure, causing premature failure of the HWH. If you have a well it already has a bladder tank so therefore one is not usually required.
  #18  
Old 02-01-2022, 08:17 AM
lpkruege1 lpkruege1 is offline
Senior Member
Join Date: Feb 2020
Posts: 168
Thanks: 386
Thanked 184 Times in 81 Posts
Default Repair or replace

Quote:
Originally Posted by Greenjade View Post
I recently noticed the paint on my garage wall near my water heater was looking a little off color. When I scraped the peeling paint I found the drywall was wet underneath.

Has anyone else had the same issue?

My house is a 2007 designer cypress The tank is on a wooden box at the back of the garage in plain sight.

State Select gas water heater with a expansion tank on the top

Possibly leak from a rusting tray?

Any advise about repairing this?

Approach the gas utility?
The pressure relief valve is leaking. They can be replaced. They come in different lengths so you would need to take it along or your repair person needs to have a selection with them. Check your water temperature to make sure you don't have it set too hot. The other issue is the pvc pipe is dripping past the pan. If you wouldn't have noticed the wall you probably wouldn't have noticed the leak. Having said that, water heaters typically need to be replaced every 15 to 20 years. So, do you repair or replace it?
  #19  
Old 02-01-2022, 08:27 AM
nancyre nancyre is offline
Senior Member
Join Date: May 2017
Location: Pine Ridge
Posts: 210
Thanks: 173
Thanked 77 Times in 52 Posts
Default

Can anybody tell me WHY the water heater is on a wooden box? I understand if it is gas and in a garage but why if electric and inside the house? What a waste of space
  #20  
Old 02-01-2022, 08:37 AM
jrref jrref is offline
Gold member
Join Date: May 2021
Posts: 1,043
Thanks: 392
Thanked 642 Times in 338 Posts
Default

Quote " The WH is original as far as I know and the house was built in 2007"

What???

We have talked about this topic over an over but as many have said, Hot water heaters, generally last from 6 -12 years depending on the brand and model. The fact that the pressure release valve is opening means there is excess pressure in the tank and that's very dangerous. It's probably from the expansion tank being bad. They only last about 5 years and need to be replaced.

At this point instead of an approximate $1,200 tank replacement, you now have a way more expensive job on your hands. This is why you should always look at the label on your tank to find out how long it's warrentied for and replace it, whether it needs it or not, within a year after the warrenty, at your convenience. If you do this when the tank is replaced the plumber will check everything and replace the expansion tank, etc, and the chances of you having a problem will be extreemly low. Some might say wait until the water heater leaks before replacing it or repair a very old water heater, or say the pan will catch the water and there is a drain to the outside of the house so don't worry BUT after the warrenty period of the tank ends you are gambling on when the water heater will fail. Sure you will have the homeowner say "my water heater lasted 25 years no problem" but you will also see many tanks will have a serious leak sometimes unnoticed causing mold and or the tank will let go and flood your house. Since you will never know when the tank will fail it's always best to just change it the following year or two after the warrenty period at your convenience. Rheem has a new water heater tank called Gladiator that has a built in water sensor and shutoff valve right on the tank to catch leaks. It's only a little more expensive than the "regular" grade Rheem tank and is more efficient.

You can check your expansion tank easily by tapping on the tank. You can flip your finger on the lower side and then the uper side of the tank or tap with a screw driver handle. The bottom should give you a thud sounding tap while the upper part should sound hollow. If both the bottom and the top sound the same like a thud sound then the bladder inside the tank has failed, it's not regulating the pressure in you hot water system anymore since the water in the system expands and contracts with temperature, and you need to replace it. You can also check the pressure in the expansion tank via the pressure valve on top of the tank. It should read about 40-65 lbs depending on the water pressure from the street. On some of these expansion tanks they were installed in such a way where it's hard to take a pressure reading. These tanks usually only last about 5 years.

That said, if your expansion tank is bad it's easily changed by your local plumber or you can do it yourself BUT make sure who ever changes it, that they pressurize the tank BEFORE installation to the approximate water pressure from the street or it will fail prematurely. I discovered that some plumbers skip this step since the tank comes prepressurized at 40 lbs. The instructions that come with the tank have the pressurizing step in big bold type so you need to do this no matter what the plumber says. Once this is done, when you drain the water heater yearly, ( and you will say "Who does this?" lol ), while the heater is drained you can check the pressure on the expansion tank and with a bicycle pump, pump it up to the correct pressure then re-fill the heater.

If you follow this basic maintenance as i said, the probability of having a problem with your hot water tank will be extreemly low.

Last edited by jrref; 02-01-2022 at 09:11 AM.
  #21  
Old 02-01-2022, 08:45 AM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,904
Thanks: 3
Thanked 7,929 Times in 2,880 Posts
Default

Quote:
Originally Posted by nancyre View Post
Can anybody tell me WHY the water heater is on a wooden box? I understand if it is gas and in a garage but why if electric and inside the house? What a waste of space
If your house is like our house, that wooden box is NOT empty, it has part of the HVAC air return duct work in it.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #22  
Old 02-01-2022, 08:50 AM
jrref jrref is offline
Gold member
Join Date: May 2021
Posts: 1,043
Thanks: 392
Thanked 642 Times in 338 Posts
Default

It's not common for the pressure release valve to be leaking unless there is excessive pressure in the tank. It's a very common mistake to replace the pressure release valve without checking the whole system first. Also while your hot water heater can possibly last 15 - 20 years, after the warrenty period you are gambling. It could fail at any time in many ways. In this case the owner could have changed the tank at 6-10 years for example and avoided this platform repair job. In some cases the leak can cause mold and that compounds the problem. So at the end of the day you are going to pay either way and you might as well change the heater at regular intervals and avoid a costly and involved repair or even worse a huge flood. As far as getting a new heater. I would recommend getting a quote from the local guys and Home Depot. Home Depot uses a very good plumbing contractor and the whole process is very simple.

Last edited by jrref; 02-01-2022 at 08:57 AM.
  #23  
Old 02-01-2022, 08:52 AM
daca55's Avatar
daca55 daca55 is offline
Senior Member
Join Date: Dec 2011
Location: Dover, NH, Village of Buttonwood
Posts: 462
Thanks: 28
Thanked 197 Times in 111 Posts
Default

If the expansion tank no longer has the correct air pressure (60psi) it will cause the pressure valve to leak. You should check the air pressure on the expansion tank. If the air pressure is less than 60psi you will need to add air to the expansion tank to bring it to 60psi. The fitting on the expansion tank is similar to a valve stem on a car tire. You can get a gage with that type of fitting at Lowes or Home Depot so you can check the air pressure in the expansion tank. Your leak may be solved by just adding air to the expansion tank.
  #24  
Old 02-01-2022, 09:07 AM
Proveone Proveone is offline
Senior Member
Join Date: Mar 2015
Posts: 180
Thanks: 80
Thanked 135 Times in 73 Posts
Default

Quote:
Originally Posted by Greenjade View Post
I recently noticed the paint on my garage wall near my water heater was looking a little off color. When I scraped the peeling paint I found the drywall was wet underneath.

Has anyone else had the same issue?

My house is a 2007 designer cypress The tank is on a wooden box at the back of the garage in plain sight.

State Select gas water heater with a expansion tank on the top

Possibly leak from a rusting tray?

Any advise about repairing this?

Approach the gas utility?
It could also be the condensation drain from your air handler is plugged.
  #25  
Old 02-01-2022, 09:14 AM
OhioBuckeye OhioBuckeye is offline
Sage
Join Date: Sep 2015
Posts: 2,545
Thanks: 1
Thanked 554 Times in 425 Posts
Default

Apparently you don’t have the water heater sitting on a water heater tray? Or you have a leaky pipe in the wall or moisture is getting in there from something else. Hum, I would have someone look at it!
  #26  
Old 02-01-2022, 10:11 AM
JP's Avatar
JP JP is offline
Veteran member
Join Date: Mar 2011
Location: The Village of St. James and Marquette, Michigan
Posts: 924
Thanks: 7
Thanked 282 Times in 125 Posts
Default

It looks like your relief valve drain pipe is not going into your water tank tray and the relief valve is being triggered repeatedly over time. I would reduce your water heater temperature and see if that helps. If not, I would put on a new relief valve and/or expansion tank.
__________________
"I am a great believer in luck, and I find that the harder I work, the more I have of it." -Thomas Jefferson
  #27  
Old 02-01-2022, 10:13 AM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 14,580
Thanks: 7,333
Thanked 5,953 Times in 3,055 Posts
Default

Quote:
Originally Posted by Greenjade View Post
I ran the hot water and put a cup under the pvc pipe that runs from the pressure release valve and after a while it had about an ounce or two of water in it. I have now put a small bucket there to catch the water. You can see from the photos that the water supply is on the back wall of the garage near the top of the WH but the water damage is on the adjacent wall near the wooden box that has the metal drain pan on it.

The WH is original as far as I know and the house was built in 2007

Could I just need a new drain pan and some repair to the water damage or it it best to replace the WH at the same time.

Does the pressure release always release a bit of water or is it kaput
IMO I would just replace the water heater (it’s only going to cause more problems) knock out all the birds (problems) with on stone (at once) then it will be good to go for another 15 plus years.

The stand probably made out of 2 by 4s, or may be metal? Probably just have to replace drywall covering it up.

Last edited by Topspinmo; 02-01-2022 at 10:22 AM.
  #28  
Old 02-01-2022, 10:14 AM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 14,580
Thanks: 7,333
Thanked 5,953 Times in 3,055 Posts
Default

Quote:
Originally Posted by nancyre View Post
Can anybody tell me WHY the water heater is on a wooden box? I understand if it is gas and in a garage but why if electric and inside the house? What a waste of space
Codes.
  #29  
Old 02-01-2022, 10:24 AM
Topspinmo's Avatar
Topspinmo Topspinmo is offline
Sage
Join Date: Dec 2012
Location: Somewhere over the rainbow
Posts: 14,580
Thanks: 7,333
Thanked 5,953 Times in 3,055 Posts
Default

Quote:
Originally Posted by Proveone View Post
It could also be the condensation drain from your air handler is plugged.
Depends on house style, my house has no connection between water heater and A/C heating system. So the A/C drain now where near water heater.
  #30  
Old 02-01-2022, 10:25 AM
davbrindle davbrindle is offline
Junior Member
Join Date: Mar 2010
Location: Bonita
Posts: 25
Thanks: 12
Thanked 23 Times in 9 Posts
Default Expansion Tank

Quote:
Originally Posted by Greenjade View Post
I ran the hot water and put a cup under the pvc pipe that runs from the pressure release valve and after a while it had about an ounce or two of water in it. I have now put a small bucket there to catch the water. You can see from the photos that the water supply is on the back wall of the garage near the top of the WH but the water damage is on the adjacent wall near the wooden box that has the metal drain pan on it.

The WH is original as far as I know and the house was built in 2007

Could I just need a new drain pan and some repair to the water damage or it it best to replace the WH at the same time.

Does the pressure release always release a bit of water or is it kaput
Time to replace the expansion tank; easy DYI, shut off supply valve to tank, open any hot water faucet to relieve pressure, Unscrew tank (turn counter clockwise). Be careful, the tank will weigh around 16 pounds, water @8#/Gal times two. Tank can be put out with trash. Most installaytions don't require pipe dope or tape as they have a gasket-ed fitting.
Closed Thread