electric receptacle installed in lamp post

Closed Thread
Thread Tools
  #1  
Old 01-30-2023, 04:36 PM
waltwl waltwl is offline
Member
Join Date: Sep 2012
Posts: 34
Thanks: 24
Thanked 11 Times in 5 Posts
Default electric receptacle installed in lamp post

anyone have a electric receptacle installed in lamp post
  #2  
Old 01-30-2023, 04:42 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,218
Thanks: 1,607
Thanked 1,744 Times in 705 Posts
Default

Quote:
Originally Posted by waltwl View Post
anyone have a electric receptacle installed in lamp post
Yes. Many have them. Several things to consider.

1) Is the circuit on your lamppost GFCI protected. Depending on where you live in The Villages, some are, some aren't. It's important to know your particular status.

2) If it is GFCI protected, you can install an appropriate receptacle box, which will include a TR/WR receptacle, and an in-use cover.

3) If it is not GFCI protected, you'll need an appropriate receptacle box, to include a WR/TR GFCI receptacle and an in-use cover.

Lastly, avoid the receptacles that are curved and match the contour of the lamppost. There are often sold by local vendors. These are not NEC compliant, as they do not provide in-use protection.

If you have any doubts, and are not confident in tackling this job by yourself, hire an electrician.

Last edited by photo1902; 01-30-2023 at 04:59 PM.
  #3  
Old 01-31-2023, 10:38 AM
n8xwb n8xwb is offline
Senior Member
Join Date: Aug 2007
Posts: 400
Thanks: 8
Thanked 336 Times in 96 Posts
Default

I just read the previous reply -- I have no idea how accurate the information is. That being said, I do know that I installed an outlet on my post 5 years ago. It is curved. I have used it everyday, 24 hours a day to keep my PHEV (plug in hybrid electric vehicle), a Chevy Volt charged. It is handling 12 amps, rain or shine. It is on a circuit that also is used for the attic light and the garage door opener. It is not GFCI protected. I have had no problems with it. I live in a courtyard villa in Sabal Chase.
  #4  
Old 01-31-2023, 03:51 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,893
Thanks: 3
Thanked 7,896 Times in 2,872 Posts
Default

Quote:
Originally Posted by n8xwb View Post
I just read the previous reply -- I have no idea how accurate the information is. That being said, I do know that I installed an outlet on my post 5 years ago. It is curved. I have used it everyday, 24 hours a day to keep my PHEV (plug in hybrid electric vehicle), a Chevy Volt charged. It is handling 12 amps, rain or shine. It is on a circuit that also is used for the attic light and the garage door opener. It is not GFCI protected. I have had no problems with it. I live in a courtyard villa in Sabal Chase.
You are taking a chance by not having a GFCI receptacle installed, these are less than $20, and well worth the money. For example, you use this outlet for a set of hedge trimmers, and accidently nick the cord, you could be shocked or worse. On the other hand, every lamp post I have helped neighbors with was connected to a GFCI in the garage or a dedicated GFCI breaker.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #5  
Old 01-31-2023, 03:57 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 16,775
Thanks: 2,913
Thanked 16,008 Times in 6,272 Posts
Default

One simple option is to buy a screw-in outlet for the light bulb socket.
  #6  
Old 01-31-2023, 06:42 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,218
Thanks: 1,607
Thanked 1,744 Times in 705 Posts
Default

Quote:
Originally Posted by n8xwb View Post
I just read the previous reply -- I have no idea how accurate the information is. That being said, I do know that I installed an outlet on my post 5 years ago. It is curved. I have used it everyday, 24 hours a day to keep my PHEV (plug in hybrid electric vehicle), a Chevy Volt charged. It is handling 12 amps, rain or shine. It is on a circuit that also is used for the attic light and the garage door opener. It is not GFCI protected. I have had no problems with it. I live in a courtyard villa in Sabal Chase.
What I posted are NEC requirements, not an opinion of mine.

And to the other poster, there are absolutely parts of The Villages where post lamps are not GFCI protected. In fact when they were installed, it might not have been required by the NEC.
  #7  
Old 01-31-2023, 07:43 PM
villagetinker's Avatar
villagetinker villagetinker is offline
Sage
Join Date: Sep 2013
Location: Village of Pinellas
Posts: 10,893
Thanks: 3
Thanked 7,896 Times in 2,872 Posts
Default

I stand corrected, thank you, as I have not helped any villagers in older sections. I agree with your comments about the current code requirements. As for the prior comment about screwing in an adapter into the lamp socket, there are so many things wrong with doing this. First, the adapter has only 2 prong and NO GROUND, second the lamp is typically only energized when the sun is down, third, the lamp post sensor is NOT rated for motor type loads. Please do not do this.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV.
  #8  
Old 01-31-2023, 08:08 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 16,775
Thanks: 2,913
Thanked 16,008 Times in 6,272 Posts
Default

Quote:
Originally Posted by villagetinker View Post
I stand corrected, thank you, as I have not helped any villagers in older sections. I agree with your comments about the current code requirements. As for the prior comment about screwing in an adapter into the lamp socket, there are so many things wrong with doing this. First, the adapter has only 2 prong and NO GROUND, second the lamp is typically only energized when the sun is down, third, the lamp post sensor is NOT rated for motor type loads. Please do not do this.
I don't know about the safety of the screw-in outlets, but they do have ones with 3 prongs, and a piece of tape over the sensor will energize it. The OP didn't say he was going to plug in a motor. Wouldn't it be fine for additional lighting?
  #9  
Old 01-31-2023, 08:15 PM
photo1902 photo1902 is offline
Sage
Join Date: Nov 2014
Posts: 3,218
Thanks: 1,607
Thanked 1,744 Times in 705 Posts
Default

Quote:
Originally Posted by retiredguy123 View Post
I don't know about the safety of the screw-in outlets, but they do have ones with 3 prongs, and a piece of tape over the sensor will energize it. The OP didn't say he was going to plug in a motor. Wouldn't it be fine for additional lighting?
Aside from the aesthetics of a cord hanging down, most light fixtures are enclosed and you have to remove the top cover to change a bulb. Not to mention a large number of the light fixtures use a candelabra base(s).
  #10  
Old 01-31-2023, 08:34 PM
retiredguy123 retiredguy123 is offline
Sage
Join Date: Feb 2016
Posts: 16,775
Thanks: 2,913
Thanked 16,008 Times in 6,272 Posts
Default

Quote:
Originally Posted by photo1902 View Post
Aside from the aesthetics of a cord hanging down, most light fixtures are enclosed and you have to remove the top cover to change a bulb. Not to mention a large number of the light fixtures use a candelabra base(s).
My lamppost has 3 candelabra bulbs, and I don't need to remove the top cover to replace the bulbs. They are accessible from the bottom. And, they do sell screw-in outlets with 3 prongs for candelabra sockets. I'm not saying that you should use them, but they are available. It seems to me that you would use the exterior wall outlet to operate motorized equipment. But, you could use a screw-in outlet for temporary Christmas lights or other lighting. That is, if they are safe.
  #11  
Old 02-01-2023, 06:41 AM
Sandy and Ed Sandy and Ed is offline
Veteran member
Join Date: Oct 2013
Location: Pennecamp
Posts: 872
Thanks: 396
Thanked 750 Times in 372 Posts
Default

Quote:
Originally Posted by n8xwb View Post
I just read the previous reply -- I have no idea how accurate the information is. That being said, I do know that I installed an outlet on my post 5 years ago. It is curved. I have used it everyday, 24 hours a day to keep my PHEV (plug in hybrid electric vehicle), a Chevy Volt charged. It is handling 12 amps, rain or shine. It is on a circuit that also is used for the attic light and the garage door opener. It is not GFCI protected. I have had no problems with it. I live in a courtyard villa in Sabal Chase.
Might need to replace it when selling the house. I just had a box installed on my light pole. Electrician said I could not use a curved box that was not gfci protected since it violated code. Figured my home owner insurance would be affected so opted for what the licensed electrician recommended (he would not have installed a non-code box anyhow). Just saying…. Listen to the Tinker.

Last edited by Sandy and Ed; 02-01-2023 at 06:52 AM.
  #12  
Old 02-01-2023, 08:20 AM
lawgolfer lawgolfer is offline
Senior Member
Join Date: Oct 2020
Posts: 257
Thanks: 2
Thanked 214 Times in 121 Posts
Default

Quote:
Originally Posted by n8xwb View Post
I just read the previous reply -- I have no idea how accurate the information is. That being said, I do know that I installed an outlet on my post 5 years ago. It is curved. I have used it everyday, 24 hours a day to keep my PHEV (plug in hybrid electric vehicle), a Chevy Volt charged. It is handling 12 amps, rain or shine. It is on a circuit that also is used for the attic light and the garage door opener. It is not GFCI protected. I have had no problems with it. I live in a courtyard villa in Sabal Chase.
Having an outdoor receptacle that is not protected by a GFCI risks death or serious injury to the user. It's one thing to risk your own health, but another to risk that of the next owner of your house. Many years ago, a young father in our son's Scout Troop plugged a drill into a non-GFCI outside receptacle installed by the previous owner. He was barefoot and stepped off the concrete patio onto the lawn, and was immediately electrocuted. It wasn't merely a matter of being "shocked". Instead, he was frozen in place and could not let go of the drill. His wife found him after some period of time and pulled the plug from the outlet. The man suffered permanent brain and heart damage. He was a Phd agronomist with a large agribusiness with a promising future. Afterwards, he could remember little about agronomy or his job. Thankfully, his employer kept him on in a minor position.
  #13  
Old 02-01-2023, 08:25 AM
Captainpd Captainpd is offline
Senior Member
Join Date: Jun 2018
Posts: 188
Thanks: 248
Thanked 196 Times in 93 Posts
Default Really

Quote:
Originally Posted by retiredguy123 View Post
One simple option is to buy a screw-in outlet for the light bulb socket.
That's not an "easy" solution. That's not even a real option
  #14  
Old 02-01-2023, 09:16 AM
HospitalCoder HospitalCoder is offline
Member
Join Date: Sep 2020
Posts: 96
Thanks: 553
Thanked 53 Times in 31 Posts
Default

Quote:
Originally Posted by waltwl View Post
anyone have a electric receptacle installed in lamp post
I had one installed a couple of months ago by Ken Smillie 843-814-3391.
He is an electrician/handyman.
__________________
HospitalCoder
  #15  
Old 02-01-2023, 09:50 AM
JGibson JGibson is offline
Veteran member
Join Date: Oct 2022
Location: Paradise City
Posts: 771
Thanks: 1
Thanked 713 Times in 301 Posts
Default

Quote:
Originally Posted by lawgolfer View Post
Having an outdoor receptacle that is not protected by a GFCI risks death or serious injury to the user. It's one thing to risk your own health, but another to risk that of the next owner of your house. Many years ago, a young father in our son's Scout Troop plugged a drill into a non-GFCI outside receptacle installed by the previous owner. He was barefoot and stepped off the concrete patio onto the lawn, and was immediately electrocuted. It wasn't merely a matter of being "shocked". Instead, he was frozen in place and could not let go of the drill. His wife found him after some period of time and pulled the plug from the outlet. The man suffered permanent brain and heart damage. He was a Phd agronomist with a large agribusiness with a promising future. Afterwards, he could remember little about agronomy or his job. Thankfully, his employer kept him on in a minor position.
I’m sorry to hear this but honestly who does any drilling barefoot? Or anything electrical barefoot?

I see people out on their lawns all the time trimming bushes and whatnot barefoot. I don't get it and they obviously never sat in a construction safety class.
Don’t use power tools electrical or cordless without foot protection.