Help. I need someone who knows a little more about electrical than I do. I know enough to be dangerous.
I have a 5 year old villa, a Leviton GFCI outlet in the garage, the breaker says it's for the garage door and all outside receptacles and that's correct. I came home from a trip and the breaker wouldn't reset, so I figure it's busted and I went to my friendly Ace Hardware. He says he's got just what I need, the only one they sell , a 20 amp Leviton. So I bought it and installed it. I look at the old one and it has 15 Amp imprinted into the plastic, but a sticker on the bottom that says 20 Amp ????? Now, my spa that's hooked into one of those outside outlets starts, but then stops. The breaker nor the GCFI shuts off, just the spa jet/heater stop. So it's either the GCFI or the spa control panel ($500 plus install). I want to check the GFCI since it's a lot less expensive. So, did I possibly install a wrong GCFI, a 20 Amp where it should be a 15?? Why would the old outler have 2 different Amperages? Does it even make much difference, does the 20 just give me more capability. Now to top it off (If you're still reading) , I went to Lowes and their GCFI says 15 Amp on the box, but the actual device has 20 Amp imprinted into the plastic. This doesn't even make sense to me. Any advice is heartfelt appreciated. |
|
#2
|
||
|
||
![]() Quote:
Hope this helps.
__________________
Pennsylvania, for 60+ years, most recently, Allentown, now TV. ![]() |
#3
|
||
|
||
![]()
It's the breaker size that determines the current. If the breaker is rated 20 amp you're good to go. If it's 15 you're still safe. Receptacles are on 20 amp breakers, lighting is on 15 amp breakers. You may have been hit by lightning.
|
#4
|
||
|
||
![]()
I agree with Tinker, never replace a 15 amp breaker with a 20 amp breaker. You could burn your house down. 20 amp breakers require 12 ga wire. 14 ga wire can only use a 15 amp breaker or GFCI.
|
#5
|
||
|
||
![]() Quote:
These are basic principles. If not understood correctly a licensed electrician MUST be employed. |